Glenn Stanton
Pat Clark_2
Member Posts: 102
Glenn,
I have a question on clearance for Z-vent installed on a Burnham Boiler. The Boiler (Spirit) installation manual allows several different venting manufactures (of which Z-vent is one) and states:
Vent pipe minimum clearance to combustible
material is five (5) inches when vent is installed in a
fully enclosed (chase) application or four (4) inches
when vent is installed with at least one side open,
similar to a joist bay application.
The installation manual for Z-vent states:
System Operating Temperature 480F (249C)
Clearance Enclosed
Horizontal 8"
Vertical 4"
Clearance Unenclosed
Horizontal 1"
Vertical 1"
Does the Boiler Installation Manual take precedence over the Z-vent Installation Manual or vice versa?
Just looking for your opinion on this before I go to the AHJ.
Thanks,
Pat Clark, Bell Plumbing & Heating
Clearance Enclosed
Horizontal 8"
Vertical 4"
Horizontal 1"
Vertical 1"
Thanks,
Pat
The boiler installation manual takes precedence and as always, your local and state code overrules that!
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Thanks Glenn
Will check with them to make sure. It is less than the 6" from the older manual so that helps.
Pat Clark, Bell Plumbing & Heating0