I have a question on clearance for Z-vent installed on a Burnham Boiler. The Boiler (Spirit) installation manual allows several different venting manufactures (of which Z-vent is one) and states:

Vent pipe minimum clearance to combustible
material is five (5) inches when vent is installed in a
fully enclosed (chase) application or four (4) inches
when vent is installed with at least one side open,
similar to a joist bay application.

The installation manual for Z-vent states:


System Operating Temperature 480F (249C)

Clearance Enclosed

Horizontal 8"
Vertical 4"

Clearance Unenclosed

Horizontal 1"
Vertical 1"


Does the Boiler Installation Manual take precedence over the Z-vent Installation Manual or vice versa?

Just looking for your opinion on this before I go to the AHJ.

Thanks,

Pat Clark, Bell Plumbing & Heating

Comments

  • Pat

    The boiler installation manual takes precedence and as always, your local and state code overrules that!

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    U.S. Boiler Co., Inc.
  • Pat Clark_2
    Pat Clark_2 Member Posts: 102
    Thanks Glenn

    Will check with them to make sure. It is less than the 6" from the older manual so that helps.