Glenn Stanton
Pat Clark_2
Member Posts: 102
Glenn,
I have a question on clearance for Z-vent installed on a Burnham Boiler. The Boiler (Spirit) installation manual allows several different venting manufactures (of which Z-vent is one) and states:
Vent pipe minimum clearance to combustible
material is five (5) inches when vent is installed in a
fully enclosed (chase) application or four (4) inches
when vent is installed with at least one side open,
similar to a joist bay application.
The installation manual for Z-vent states:
System Operating Temperature 480F (249C)
Clearance Enclosed
Horizontal 8"
Vertical 4"
Clearance Unenclosed
Horizontal 1"
Vertical 1"
Does the Boiler Installation Manual take precedence over the Z-vent Installation Manual or vice versa?
Just looking for your opinion on this before I go to the AHJ.
Thanks,
Pat Clark, Bell Plumbing & Heating
I have a question on clearance for Z-vent installed on a Burnham Boiler. The Boiler (Spirit) installation manual allows several different venting manufactures (of which Z-vent is one) and states:
Vent pipe minimum clearance to combustible
material is five (5) inches when vent is installed in a
fully enclosed (chase) application or four (4) inches
when vent is installed with at least one side open,
similar to a joist bay application.
The installation manual for Z-vent states:
System Operating Temperature 480F (249C)
Clearance Enclosed
Horizontal 8"
Vertical 4"
Clearance Unenclosed
Horizontal 1"
Vertical 1"
Does the Boiler Installation Manual take precedence over the Z-vent Installation Manual or vice versa?
Just looking for your opinion on this before I go to the AHJ.
Thanks,
Pat Clark, Bell Plumbing & Heating
0
Comments
-
Pat
The boiler installation manual takes precedence and as always, your local and state code overrules that!
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Thanks Glenn
Will check with them to make sure. It is less than the 6" from the older manual so that helps.
Pat Clark, Bell Plumbing & Heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements