Cast Iron Boiler w/ Flate Plate Pool Heater
Options
hot_rod
Member Posts: 26,594
for a load that large to keep the boiler in the condensing mode for extended periods.
The best way is a mixing device or return protection mechanism. Primary secondary alone will not assure you have adequate return protection.
You need a means to watch and adjust that return temperature to the boiler.
tekmar controls, injection mixing, 3 way thermostatic valves are a few options.
hr
The best way is a mixing device or return protection mechanism. Primary secondary alone will not assure you have adequate return protection.
You need a means to watch and adjust that return temperature to the boiler.
tekmar controls, injection mixing, 3 way thermostatic valves are a few options.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
Will a flat plate heat exchanger for a pool cause damage to a convention cast iron boiler due to condensate? Return water temps are below 140* during the first start up of the day for about 5 hours. Would primary secondary pumping be a solution to prevent pre-mature cast iron failure?0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements