Cast Iron Boiler w/ Flate Plate Pool Heater

hot_rod
Member Posts: 24,726
for a load that large to keep the boiler in the condensing mode for extended periods.
The best way is a mixing device or return protection mechanism. Primary secondary alone will not assure you have adequate return protection.
You need a means to watch and adjust that return temperature to the boiler.
tekmar controls, injection mixing, 3 way thermostatic valves are a few options.
hr
The best way is a mixing device or return protection mechanism. Primary secondary alone will not assure you have adequate return protection.
You need a means to watch and adjust that return temperature to the boiler.
tekmar controls, injection mixing, 3 way thermostatic valves are a few options.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
Will a flat plate heat exchanger for a pool cause damage to a convention cast iron boiler due to condensate? Return water temps are below 140* during the first start up of the day for about 5 hours. Would primary secondary pumping be a solution to prevent pre-mature cast iron failure?0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements