Light Wall Piping For Heat Pump Loop
Chuck_17
Chuck_17 Member Posts: 148
Any opinions on lighter than Sch 40 pipe for heat pump loops for 2-1/2" - 4" with grooved mechanical couplings?
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Depends on the pressure and velocity.
    Generally Sch. 40 is the standard as you know, but for low pressure, Sch. 30 or even Sch. 10 has been used. Ugh. Also Sch. 40 PVC had a good run in the Developer '80's, but let's not go back there, shall we?
  • Marty
    Marty Member Posts: 109
    don't
    Nope uh uh no way ......but thats just my opinion :) Even schedule 40 will turn into a mess if the tower goes down on a hot day, even worse if a boiler runs wild.
  • Brad White_119
    Brad White_119 Member Posts: 11
    You of course mean
    the PVC plastic option, Marty. No concerns on the metallic pipe I take it?
    True, the PVC looked like the Loch Ness Monster or Champ the Lake Champlain serpent after a fashion.
    The Value Engineering package the contractor offered ignored our edict that hanger spacing was to more or less be half that of steel.... When pipe sags to the point that you get air pockets, you have a bigger problem.
  • Marty
    whoops
    Missed the grooved fittings then saw the letters pvc and started typing while remembering a rather spectacular failure of a pvc loop. 40 is "standard" and people are used to working with it and its usually on the shelf somewhere for whatever thats worth.
    EBEBRATT-Ed Member Posts: 19,640
    We have used schd. 10 with no problems. I wouldn't use it on any type of open system though.
    What are the code ramifications of this??????????
    Nice and light.
    Ed