Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
making a wall hung radiator
Options
ed wallace
Member Posts: 1,613
is it possible to make a wall hung radiator using copper pipe? job requires 10,000 btus per hr how large would the pipe have to be?
0
Comments
-
What water temperature, Ed?
Even if at 180 degrees, that is a lot of copper... 67 EDR more or less. If using 140 degree water, that would be 112 EDR...
I know the price of copper has dropped, but don't spend it all in one place! Your time is worth money too.
Sure, it is possible, most anything is.0 -
Wall rad.....
Take a look at Hot Rod's "copper Christmas project 08" thread.
Just shows you what's possible.There was an error rendering this rich post.
0 -
wall hung radiator
water temp would be 180 degrees 3/4 copper to and from the boiler want to do something nice and unussual for a very nice old lady0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 418 Carbon Monoxide Awareness
- 74 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 854 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements