making a wall hung radiator
ed wallace
Member Posts: 1,613
is it possible to make a wall hung radiator using copper pipe? job requires 10,000 btus per hr how large would the pipe have to be?
0
Comments
-
What water temperature, Ed?
Even if at 180 degrees, that is a lot of copper... 67 EDR more or less. If using 140 degree water, that would be 112 EDR...
I know the price of copper has dropped, but don't spend it all in one place! Your time is worth money too.
Sure, it is possible, most anything is.0 -
Wall rad.....
Take a look at Hot Rod's "copper Christmas project 08" thread.
Just shows you what's possible.There was an error rendering this rich post.
0 -
wall hung radiator
water temp would be 180 degrees 3/4 copper to and from the boiler want to do something nice and unussual for a very nice old lady0