New System performance
TGO_54
Member Posts: 327
I took the following readings on a new install, 2 ton 410A system. How is it performing? Any problems you see based on these readings?
Indoor wet bulb 62
Indoor Dry bulb 72
Supply air (right off the air handler) 47
Return air (right at the air handler) 67
Suction line pressure 128PSIG
Liquid line pressure 257PSIG
Suction Line temp (at the condensor) 50
Liquid Line Temp (at the condensor) 75
Outdoor air temp 76
System has a TXV valve and the MFG calls for 11 degrees of subcooling + - 2 degrees.
Thanks!
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=278&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Indoor wet bulb 62
Indoor Dry bulb 72
Outdoor air temp 76
Thanks!
Looks Great!
From your calculations, you have a 20-degree delta-t across the evaporator coil, a 23-degree delta-t OF the evaporator coil, 11 degrees of subcooling and a superheat of 6 degrees.
Just as a calculation error, the liquid line temperature cannot be lower than the outside ambient but, since they only differ by 1-degree, I can safely say that descrepancy is due to measurement error.
Awesome job! Who taught you air conditioning?! (Kidding)0 -
Thanks Eugene'
> Just
> measurement error.
Thanks Eugene
I will have to check the probes on my thermometer, I am sure I took the readings carefully.
The air handler has the TXV bulb inside the cabinet, and I was surprised to see it was not insulated. I called the rep about it and they told me thats the way it should be. Hard to argue with results like the ones I posted. The unit is rated at 15 seer. Can't wait until I learn enough about Pressure enthalpy to chart it.
It was a very smart man and a great teacher who is still "learning me the AC trade"
BTW - Have you chaecked your e-mail recently?
Thanks
Tom
Aw Shucks...
I'll be in touch about the e-mail.
There is a placement test involved (institution requirement) and I will find out the details for you.