F + T Traps on steam boilers
Options
Servicewiz_2
Member Posts: 28
I have a York Shipley 125 HP steam boiler that has a F + T steam trap located approx. 2 inches above the operating water line. I am having some problems with discharge from this trap. The job is only 4 years old .I have worked on many steam boilers + seen very few trapped. The trap is located by itself on the oppossite side of the McDonnell miller conrol.Any info. is greatly appreciated!
Servicewiz
Servicewiz
0
Comments
-
That would be
a spill trap. It opens only when the boiler has too much water in it.Retired and loving it.0 -
Dan knows.
These traps are used to keep a boiler from flooding. If the steam valve is left open and the boiler is idle or on standby it will fill with condensate and when it fires on a call for heat the trap keeps the water line at a safe level.
Ed0 -
i work on a lot of commercial steam --probably 50% of our accounts are steam,many with 2 boilers --out of those i have only seen 10 boilers with spill traps --what kind of "problems are you having --in the dual boiler situation --when connected to the common header w/no check valve the "cold" boiler will receive steam from the header--condense and overfill---and drain through the spill trap--if your water quality is poor,dirty,oily--etc.. --and you are surging,priming,foaming you will get a lot of discharge from the spill trap---if the traps' float,seat,or themostat is bad you will get live steam discharge,
0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements