indirect fired heater temperature pressure relief
        
            Options        
            
        
 
            
                
                    Brad White_9                
                
                    Member Posts: 2,440                
            
                        
            
                    The typical 150 PSI/210F T&P valve is what I would use. Just make sure the BTU rating meets or exceeds the boiler rating. Commonly available item. (EDIT- Yes, ASME as Paul mentioned. I do that reflexively but forgot that many commercial valves are not so rated.Thanks Paul.)                
                0                
            Comments
- 
            
 We are installing a Munchkin boiler to power a radiant floor heat system, along with a Superstor Ultra indirect fired water heater. We are using the 80-gal tank and the 199M boiler. For the temperature pressure relief valve on the water tank, do I need anything different than a typical hot water heater t-n-p valve?
 0
- 
            Relief valve
 The 80g tank requires the ASME relief valve (Watts #40) rather than the standard 3/4" 100XL which is used on conventional water tanks or the 60g indirect or smaller.
 The instructions note this in the fine print.
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            
 Really? I did not see that anywere in the manual, and I tried to be thorough. Thanks for the heads up.
 0
- 
            wanna tell us
 Thanks for the informations Paul.. Next question, what the difference between the regular relielf valve and the amse? Asides from same rating, size, paying more for amse tag?0
- 
            40XL
 The 40XL has higher ratings...not the same as the 100XL. It presumes the tank could have an input greater than 100K btu's.
 Also the 40XL has a longer stem for insertion into a tee, unless the tank has a side tapping specifically for the relief valve.
 Yes, the 40XL is pricey.
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            Some help?
 I know in the boilers we install the manufactuer recomends a 30# blowoff and code requires a regular T&P. So we use both in conjunction on the heating side with another one on the indirect tanks. Just some food for thought.
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            Do I read that correctly
 Your code requires a T&P in the boiler ??
 Scott
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            yup
 With the GB142 it is in the state of OR considered a boiler unless it has a T&P on it then it's not. Weird I know but that's OR for you. So on the primary loop package we modify it to acomdate a 30# and a regular T&P.
 So I guess it's not a code issue unless we want to spend the extra money and hassle on a boiler permit and inspection and all.
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements