GAS PIPE SIZING
Brad White_185
Brad White_185 Member Posts: 265
according to my tables for piping in general (and not sure why this would not apply), a one-inch standard elbow is worth 5.2 equivalent linear feet. (Long radius -as if- would be 2.7 ELF.)
While we are at this, a tee with straight flow would be 3.2 ELF and branch flow 6.6 ELF. A 45 elbow is worth 1.3 ELF. This is all for one-inch pipe size.
  • Paul_11
    Paul_11 Member Posts: 210
    How many equivelant feet of pipe is an elbow on 1\" gas pipe
    Can anyone help me with this.
    My copy of the fuel gas code is in my office and I need to figure this out tonight.
    How many feet of pipe should you add for each ninty degree elbow on a 1" gas line.
    Paul
    A Real Good Plumber.
    Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
    NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
    A REAL GOOD PLUMBER, INC
    NYC LMP: 1307
    O:212-505-1837
    M:917-939-0593
  • Todd S_8
    Todd S_8 Member Posts: 26
    Sizing
    I have a book from Central Hudson that says to add 5 feet for an elbow.
  • rich pickering
    rich pickering Member Posts: 276
    Canadian gas code is 2.62 feet.
  • Brad White_185
    Sure that is not
    in Meters, eh?
    I mean, our dollar is down in value compared to your guys, practically at parity, and now you go playing with our feet? What gives? :)
  • rich pickering
    Nope.
    0.80 meters.
    I use feet and inches, and fahrenheit for boiler temps but celsius for outdoor temps.
  • Brad White_185
    And I use
    furlongs per fortnight to express velocity.
    So there! :)
    Actually your 2.62 feet is roughly that of a long radius (1.5 R) elbow, the use of which I applaud. If anything they also look nicer.
  • Paul_11
    GAS PIPE SIZING
    Thanks much to all those who replyed, you were a big help.
    I am curious though, if anyone find somewhere on line where this information is available?
    Our survey determined that they need a new gas service to the building, a larger gas meter and to replace the 90' of 1" gas line with 1 1/4".
    Another case of this job costing a lot more to go with the "low bid".
    Thanks
    paul
    NYC LMP: 1307
    O:212-505-1837
    M:917-939-0593
  • bob_46
    bob_46 Member Posts: 813
    Pressure
    Paul, contact your gas supplier and see if they can change the service to 2PSI. Add a Lbs to inches regulator at the end and your good to go.
  • Brad White_187
    Brad White_187 Member Posts: 13
    Code
    Here in MA at least, we cannot have over 0.50 PSIG (14" WC) gas inside a building, at least without a special permit. Just a point to ask in your locale.
    My $0.02
    Brad
  • Brad White_187
    On-Line Resource
    When my books are not nearby, this is a handy site I have found for lots of quick look-ups:
    http://www.engineeringtoolbox.com