Old Stuff
Jeff Lawrence_25
Member Posts: 746
A few weeks ago, I did a change out of a 11 year old system. I posted some pictures of the lack of condensate drain, but never really looked a the coil closely.
That changed yesterday.
I recycle scrap and really looked at the coil. It wasn't your typical coil. Here's a first shot of the coil.
Here
This is the other shot.
This isn't the normal finned coil that is out there now.0 -
The system
Was first installed in about 1965 by the homeowner.
Here's the expansion valve. Notice anything?
The liquid line was a 1/2" copper that had been reused when the original system (furnace and outside unit) was replaced 11 years ago. The suction line was 1 inch water line that was soldered, not brazed.0 -
The most amazing thing
Was the thermostatic expansion valve.
Make you wonder how it worked.
The clickable picture is the same, only full sized.0 -
better picture
maybe...0 -
Yes
That is a R12 expansion valve on the system. It (the coil OR the TXV) wasn't changed when they put the new furnace and condensing unit.
How did it work?
It did, according the the homeowner.0 -
Aerofin
Looks like an Aerofin coil also used by Buffalo Forge and still available I think. The fins were turned off of heavy wall soft tubing on a pattern lathe then fitted to headers. Sometimes the entire assembly would be "solder-dipped" and that may account for the silvery color. The fin-to-tube bond is inherent with that manufacturing method.
Nope
The fins are aluminum and the tubing is copper. You can pull the fins off fairly easily and they come off as a spiral, meaning the fins are more or less one peice.
I've seen what you're talking about at a boiler factory.0 -
The Trane was finally Stopped!
Hey Jeff
GE or Trane unit? Saw a coil like that in an old GE unit. Did not have a R-12 TXV that I know of, but did have the same evap coil.
According to counter personal, the orfice may be ok for R-22 depending on what tonnage you have compared to the R-12 size.
Look at Sporlan's Q-valve kit, and you can see how the orfices are the same for all refrigerants, just different sizes. Anyone doing refrigerantion should have a Sporlan Q-BQ valve kit.
Don in MO0 -
The coil
Was a Carrier. The system I replaced was a Lennox, only 11 years old. As I recall, it was a 3 ton system.0 -
Old Stuff!
Morning!Hay Jeff!Way back then, Carrier had R500 which acted very close to R12. Possible?Enjoy Your Day!0 -
old coil
ran across something like that last year old carrrier.had air handler by changind the expansion valves and linesets you could chaNGE THE COOLING CAPACITY.0 -
ANY BODY EVER HEARD OF INTERNATIONAL COOLING PRODUCTS .CUSTOMER CALLED HAS A COIL AND CONDENSING UNIT INSTALLED IN 1970 WITH NO MAINTENANCE.GOT HIS MONIES WORTH.0 -
ICP-
Is a division of Carrier/United Technologies.0 -
I'll bet
the customer is fussing about having to replace the system.
You're right, the house got the money's worth out of it.
Anything's possible
It could have been a Carrene unit. I've actually worked on one of those many years ago.0 -
Old Stuff
Morning! I stillhave a 30lb drum of r500 in my shop.Good Day All!0 -
Nice Pics Jeff
Leave it to you to dig up all of the old goodies in Atlanta...
Hope you're having a great summer.
As far as the R-12 TXV is concerned, I have seen it done. The trick is to lower the spring pressure as low as possible without having the superheat spring adjust shoot out of the bottom of the valve. If such is the case, you'll be operating the evaporator with about 30 degrees of superheat. Of course this is not the ideal situation but, back in the days of old, there was little attention paid to efficiency. The goal was to get the Darn thing to blow cold air.. Period....
