5psi to get Mercury Switch to Trip
TomBk
TomBk Member Posts: 2
Boiler was not responding to thermostat and I had to crank the pressure up to 5psi to get the mercury switch on the pressuretroll tilted back enough for it to trip and the boiler to come on. The pressuretroll and pigtail hasn't moved since it was working right with about 1.5psi differential. The pressuretroll is very old though.
Any ideas on what steps I should take to troubleshoot?
  • ttekushan_3
    ttekushan_3 Member Posts: 965
    clog
    The pigtail its mounted to is clogged.
    When everythings back together make sure the pressuretrol is LEVEL.
    Terry T
  • Ed_13
    Ed_13 Member Posts: 164
    Cleaning out the pigtail did it
    That did it. Thanks. Regards, Tom
  • tom_82
    tom_82 Member Posts: 66
    pressuretrol
    just curious.
    When your pressuretrol is working can you actually see the switch (mercury) move?
    I have stared at ours as intently as i've stared at anything in my life and it does not move a millimeter.
    Thanks
    TOm
  • tom_82
    pressuretrol
    just curious.
    Thanks
    TOm