5psi to get Mercury Switch to Trip
TomBk
Member Posts: 2
Boiler was not responding to thermostat and I had to crank the pressure up to 5psi to get the mercury switch on the pressuretroll tilted back enough for it to trip and the boiler to come on. The pressuretroll and pigtail hasn't moved since it was working right with about 1.5psi differential. The pressuretroll is very old though.
Any ideas on what steps I should take to troubleshoot?
Any ideas on what steps I should take to troubleshoot?
0
Comments
-
clog
The pigtail its mounted to is clogged.
When everythings back together make sure the pressuretrol is LEVEL.Terry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0 -
Cleaning out the pigtail did it
That did it. Thanks. Regards, Tom0 -
pressuretrol
just curious.
When your pressuretrol is working can you actually see the switch (mercury) move?
I have stared at ours as intently as i've stared at anything in my life and it does not move a millimeter.
Thanks
TOm0 -
pressuretrol
just curious.
When your pressuretrol is working can you actually see the switch (mercury) move?
I have stared at ours as intently as i've stared at anything in my life and it does not move a millimeter.
Thanks
TOm0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements