Solo 250 in monoflo tee system
[Deleted User]
Posts: 0
Use the properly sized circ for the boiler and a Wilo Stratos for the System you will have no problems running the system with outdoor reset coming off of the boiler.
0
Comments
-
Solo 250 in monoflo tee system
System currently has two (2) CG 210 gas units injecting into a monoflow system with a giant TAco circ. All cast iron rads. I did the heatloss being pretty conservative and came up with 199K. I was thinking about using a Solo 250, piping directly through the boiler, no P/S, and controlling it with a Tekmar control with indoor feedback. I guess I am talking about constant circulation, though I have never done this before.
Ideas on this and controls, etc.
Thanks,
Rob0 -
I would use 2 pumps, 1 appropriate for system and 1 for the boiler, wired in parallel with the boiler control.
T the boiler into monoflo system like a injection system.0