victaulic piping/boilers
I have a bunch of boilers with victaulic piping. Ususally coming out of the boiler it is ips and we put a ips/ vic nipple.
  • victaulic piping/boilers
    did i read it here about vic and boilers? and if not here, has anyone heard/used it? the vic catalog lists high temp, (250-300deg) gasketry, so.........
    EBEBRATT-Ed Member Posts: 19,598
    The last I new the boiler code in MA. required all components to be rated 250 F. Vic I beleive is rated less than that 220?? or something??.
    Then I was told by a state inspector that vic was ok but can not be used on "the first conection" at the boiler.
    Other than that we have used vic on heating with no problems.
    ED
  • interesting
    vic does list 250deg gaskets for "hot water". but i wasn't sure about continous high temps
    thanks
  • Keith_8
    Keith_8 Member Posts: 399
    Vic
    We use vic on our larger HW boiler installs. No problem, the only thing I would stay away from is the reducing clamps. We have had problems with leaks showing up after a period of time. Now we only use a true reducing coupling.
    Pay attention to the type of clamps you use and the chemicals that may be in the system. The rubbers are rated for different chemicals as well as temperatures.
    Keith
    Keith
  • yeah keith,
    i noticed the vic chemical rated gaskets, but hadn't given it a thought at the time
    have any info on steam compatibility?
    Vic is not steam compatible.
    Ed
  • Pat_11
    Pat_11 Member Posts: 50
    Vic fittings
    the Mass Dept of public safety states the following. I would think this covers vic fittings.
    14.02: Board Interpretations
    (4) June 23, 2003 – Use of specialty clamped pipe fittings
    The Board has taken the position regarding the use of specialty clamped pipe fittings and will allow their use provided they meet the temperature and pressure requirements of the code. In cases where the gasket material does not meet the temperature range of the boiler, the high temperature limit shall be turned down to meet the temperature limitations of the clamped fitting. If the temperature limit is dialed back, the maximum temperature setting must be indicated on the certificate of inspection.
    Regards,
    Pat