How to power multiple zone valves
Al Corelli
Al Corelli Member Posts: 454
I asked this question not even a week ago. I was told that up to 4 thermal heads can be multiplexed onto one "zone".
    hot_rod Member Posts: 26,579
    on a radiant manifold for example
    I use the Taco zone control module. On one zone I have 3 loops with heat type actuators. Can I power 2 or more actuators from one Taco connection? Or better to custom build a transformer and relays?
    hr
  • jp_2
    jp_2 Member Posts: 1,935
    second guess?
    taco should provide amperage & voltage data on the contacts, I hope? this IS standard other places.....
    I see the 80VA
    worth of transformer on the 6 zone controller. And I know the current draw of the actuators. I wasn't sure how many actuators could go on one set of terminals below the t-stat connections.
    hr
  • jp_2
    i'm planning to
    use an Omron ZEN programmable relay, taco should look out !
    gives me more flexibility.
  • Darrell
    Darrell Member Posts: 303
    I've been told by the Taco Rep, and have done so successfully, to jump the related t-stat contacts, observing polairity, on the Taco ZVC so that one t-stat will operate miltiple zonevalves or actuators. No resistors or other magic is needed and the anticiaptor on the T-stat can be set as you would for a single zone valve.
    I have to do this frequently when small zones don't get along and turn each other off. I pick a more centrally located T-stat and make it the operative control for multiple small zones.