heat loss calc
Mike T., Swampeast MO
Member Posts: 6,928
Haven't used that particular worksheet, but it should be reasonable if not as easy and in-depth as a good computer program.
Loss through the ceiling when there is heated space above is ZERO so don't even consider. Same as a floor when there is heated space below.
heat loss calc
since I can't find a contractor who seems willing to do a heat loss calc I thought I try myself. I've got the I=B=R calc sheet 1502 off the slantfin website. I'm curious to hear from those more knowledgable then myself whether this will do a good job of estimating boiler size for my home. Also could someone tell me whether the section to calculate ceiling loss is relevant for the first story of a two story house? It would seem to me that the heat rising through the first floor ceiling is still contained in the house (second floor).
Thanks in advance
scott0 -
+slant fin will send you free
a heat loss calculator on disc. It only takes about a week. Click on the link at the bottom left for heat loss calculations0 -
Still waiting for mine
Back in the day..........I haven't used that in a long time. Computer based load calcs are so much less time consuming.
That being said, when I did use that method it seemed to be accurate. IE; I never ran into trouble with undersizing or grossly oversizing equipment. The caveat as with all heatloss/gain methods is that they are only as accurate as the input figures you provide.0 -
Slant Fin
they also offered it on the web site as a download I think?
PATRIOT HEATING & COOLING, INC.