Tekmar 260 questions
Joe Brix
Member Posts: 626
On a 260, is there any way to change the target temp of 180° on a DHW call? Does this override the Max boiler temp if set below 180°?
If boiler min temp is set, is it maintained during WWSD?
I also don't understand the purpose of the fire delay time setting. On a boiler demand, what does this change? Will the 260 wait to run the circulator until the boiler begins firing?
tekmar 260
Hello John,
The 260 operates the boiler at 180F during DHW Demands. The boiler max setting always overrides all other settings, so yes, if the boiler max setting is below 180F, the boiler max setting will be the operating temperature during a DHW Demand.
The boiler minimum temperature is only maintained when there is a boiler demand or DHW demand.
Warm Weather Shut Down (WWSD) causes the 260 to ignore Boiler Demands, thereby shutting your heating system off for the summer. The boiler minimum temperature is not maintain during WWSD.
The fire delay setting accounts for any pre-purge and ignition time on the boiler. Close the boiler TT terminals and use your watch to time how long it takes for the burner to turn on.
The 260 primary pump turns on immediately if only a Boiler Demand is present and the control is not in WWSD.
If you have additional questions, please contact your local tekmar representative or call tekmar direct. A list of tekmar rep's are listed on the tekmar website. www.tekmarcontrols.com
Jay Vath
tekmar Control Systems0 -
Thanks Jay
That clears up all my questions. You're a great resource to have on this site. Tekmar has some real solid products.0