Another vaporstat question...
Options
Bob W._3
Posts: 561
This is probably for Steamhead, if he is reading...
You have convinced me to go to a vaporstat with my downsized boiler. Which one should I ask my contractor to supply? Some go 0-4lb. while the ones for vapor systems go 0-16oz. Also, some break on pressure rise, etc. I checked State Supply and they list the following Honeywell vaporstats: L408A1157, 1132, 1131, 1149, 1046 and 1053. Thanks again.
Bob
North Mankato, MN
You have convinced me to go to a vaporstat with my downsized boiler. Which one should I ask my contractor to supply? Some go 0-4lb. while the ones for vapor systems go 0-16oz. Also, some break on pressure rise, etc. I checked State Supply and they list the following Honeywell vaporstats: L408A1157, 1132, 1131, 1149, 1046 and 1053. Thanks again.
Bob
North Mankato, MN
0
Comments
-
two choices
If you are absolutely certain that the whole system will fill with steam at about a half pound of pressure, the 0-1 PSI vaporstat gives really good control, where the 0-4 PSI one isn't as sensetive operating under a pound of steam pressure.
Noel0 -
Thanks Noel. Should I get one that breaks on pressure? I am thinking that would be the logical choice for a simple single pipe non-vapor system.0 -
breaks on pressure RISE
as opposed to makes on pressure rise.
Correct, you want the one that breaks on pressure rise.
Noel0 -
Many thanks. Boy, this Wall is a great place.0 -
I'll second
both of you!0
This discussion has been closed.
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements