Another vaporstat question...

Bob W._3
Bob W._3 Member Posts: 561
This is probably for Steamhead, if he is reading...

You have convinced me to go to a vaporstat with my downsized boiler. Which one should I ask my contractor to supply? Some go 0-4lb. while the ones for vapor systems go 0-16oz. Also, some break on pressure rise, etc. I checked State Supply and they list the following Honeywell vaporstats: L408A1157, 1132, 1131, 1149, 1046 and 1053. Thanks again.

Bob
North Mankato, MN

Comments

  • two choices

    If you are absolutely certain that the whole system will fill with steam at about a half pound of pressure, the 0-1 PSI vaporstat gives really good control, where the 0-4 PSI one isn't as sensetive operating under a pound of steam pressure.

    Noel
  • Bob W._3
    Bob W._3 Member Posts: 561


    Thanks Noel. Should I get one that breaks on pressure? I am thinking that would be the logical choice for a simple single pipe non-vapor system.
  • breaks on pressure RISE

    as opposed to makes on pressure rise.

    Correct, you want the one that breaks on pressure rise.

    Noel
  • Bob W._3
    Bob W._3 Member Posts: 561


    Many thanks. Boy, this Wall is a great place.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    I'll second

    both of you!