Could this be right?
scott markle_2
Member Posts: 611
Rethink the .6 part of it. 120 is only half the story. it's about delta, assuming 20 deg. delta .6 gpm = 6000 btus. If your spacing is 6" and if all 226' of your tubing was on the floor. 226x.5 =113 sq.ft of heated floor. let's be generous and give you 30 btus/sq.ft 30x113= 3339 or .33 gpm at 20 deg. delta.
GPM=BTU/500X∆T hence 3339/10,000=.33
Try and keep those 5/16 loops under 200 or so and get your heat loss under control and your head pressures should be more reasonable.
Upunor pressure drop calculations.
I am calculating pressure drop in a 226' loop of 5/16'pex tubing. The flow rate is .6gpm and I have a supply temp. of 120. I calculated the pressure drop to be 32' head. Could this be right or am I doing something wrong? From my CDAM I am using a factor of .14171/ft. I forgot to mention that this is for 100% water.
Please help.
Thanks.
Dan Sedens0 -
Pressure drop calculations
That would be correct.
See attached Viega Tech Datasheet - page 2.
A GPM of 0.6 is too much flow for 5/16" tubing. That requires a pressure drop of 15 psi.
Doug0 -
oops
.33 not 3.30 -
Thanks for the help
Guys,
Thanks for the input. I was trying to run a 10 Delta. Works much better with a 20 Delta. All is good now.
Again, Thanks for the help.
Dan Sedens0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam