Could this be right?

Rethink the .6 part of it. 120 is only half the story. it's about delta, assuming 20 deg. delta .6 gpm = 6000 btus. If your spacing is 6" and if all 226' of your tubing was on the floor. 226x.5 =113 sq.ft of heated floor. let's be generous and give you 30 btus/sq.ft 30x113= 3339 or .33 gpm at 20 deg. delta.

GPM=BTU/500X∆T hence 3339/10,000=.33

Try and keep those 5/16 loops under 200 or so and get your heat loss under control and your head pressures should be more reasonable.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Dan Sedens
    Dan Sedens Member Posts: 48
    Upunor pressure drop calculations.

    I am calculating pressure drop in a 226' loop of 5/16'pex tubing. The flow rate is .6gpm and I have a supply temp. of 120. I calculated the pressure drop to be 32' head. Could this be right or am I doing something wrong? From my CDAM I am using a factor of .14171/ft. I forgot to mention that this is for 100% water.

    Please help.

    Thanks.

    Dan Sedens
  • Doug_7
    Doug_7 Member Posts: 266
    Pressure drop calculations

    That would be correct.

    See attached Viega Tech Datasheet - page 2.

    A GPM of 0.6 is too much flow for 5/16" tubing. That requires a pressure drop of 15 psi.

    Doug
  • scott markle_2
    scott markle_2 Member Posts: 611
    oops

    .33 not 3.3
  • Dan Sedens
    Dan Sedens Member Posts: 48
    Thanks for the help

    Guys,

    Thanks for the input. I was trying to run a 10 Delta. Works much better with a 20 Delta. All is good now.

    Again, Thanks for the help.