Propane BTU calculation?
There are approx. 91,000 BTU's available in a gallon of propane, so multiply 2.4 x 91K and you get 218,400 BTU....at 100% efficiency.....multiply that by the efficiency rating of the unit to get approx. BTU consumption.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=248&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • Jamie_6
    Jamie_6 Member Posts: 710
    Propane
    How do I convert the following information into BTU's?
    88 cubic foot per hour / 2.4 gallons per hour Propane.
  • Al Letellier_9
    Al Letellier_9 Member Posts: 929
    > BTU's?
    > per hour Propane.
    > _A
    > 289&Step=30"_To Learn More About This
    > "Find A Professional"_/A_
  • Constantin
    Constantin Member Posts: 3,796
    Isn't Propane 91.6kBTU/Gallon?
    ... so looks like 220kBTU/hr...
    EDIT: Looks like Al beat me to the answer! :-P
    Ah, the joys of a laggy internet connection and tabbed threads...
  • Dick Charland
    Dick Charland Member Posts: 178
    Could be
    Constantin, but who knows for sure that it is to spec. We figure #2 oil at 142,000, but that may not always be the case.
  • S Ebels
    S Ebels Member Posts: 2,322
    Supposedly it is........
    There is however, variation in blends that yield different btu/gallon numbers. I was told by a large local propane company to use 90,000 to be safe. They sell over 6,000,000 gallons per year so I assume they know whereof they speak.
  • Bob Harper
    Bob Harper Member Posts: 1,134
    BTU values
    The stated BTU values are a function of the vapor density/ specific gravity. The heavier the fuel, the higher the BTU rating. Same with NG. Depending upon where you live. Around Philly, PECO says use 1050 BTU/ Cu ft. That, however does not take into account "spiking" during high demand periods where they toss in whatever is lying around on the back shelf---butane, ethane, iso-ethyl whazzamattathane. You name it. Of course, they'll deny it or play it down but just wait until the LNG flows. Get out your Wobbe Index numbers!
    Timmy? Ed?