Water too hot
jeff_51
jeff_51 Member Posts: 545
could be fed off of the water on the steam boiler. With a five family building, that would prolly get you the most hot water at the lowest cost, and with it's own pump and stat, you would solve your overheating issue. More money up front, but would be the better course in the long run I would think Go to heating Q&A and then the thread condensate hot water heating. This would apply to a domestic hot water maker as well.
  • Jonathan_7
    Jonathan_7 Member Posts: 2
    Water too hot during heating season
    When our boiler is producing steam for the radiators the domestic hot water is too hot, even if we set the temeperature as low as 120 degrees. If the steam isn't on, the hot water is fine. How do I start troubleshooting this?
  • Big Ed
    Big Ed Member Posts: 1,117
    Auto Mix
    I recommend a seperate hot water heater over a coil.It will solve half of your water problems...But if you like a coil ,install a auto mixing valve to regulate tap temperature....
    P.S. pipe in as per instructions
  • Jonathan_7
    Further recommendations?
    Thank you for that prompt response. Would a separate water heater require a separate burner?
    The auto mixing valve is a compelling suggestion - I didn't know such a device existed. Our building is a 5-family, just to give you an idea of the application. Is there any particular valve manufacturer you would point me to towards?
  • honeywell makes
    a nice mixing valve that will limit the high temp water that comes out of your boiler. Bob
  • bob young
    bob young Member Posts: 2,177
    HOLBY
    check out HOLBY mixing valves. it is the cadilac & you will not be sorry you installed it.