\"Splitting\" a Steam Radiator
Options
Dave_127
Member Posts: 18
I have one-pipe steam heat in my 50-year-old house. I am splitting the upstairs bedroom farthest from the boiler into two rooms. I would like to "T" the steam line that goes to the current single radiator to supply two radiators, one in each room. My plumber says you can't "T" a steam line.
(By radiator, I mean the kinds with a row of sheet metal fins enclosed in a metal housing, not the big cast iron radiators of old.)
There are 8 radiators in my house and not 8 steam lines leaving the boiler, so I know that radiators can share a steam line.
Can I "T" the steam line? What are the issues/problems?
Do I simply need to use a "Y" instead of a "T" so the water can run back down?
If I can't "T" the radiators, can I feed one radiator, then pipe out of that radiator a short distance through the wall into the second radiator, terminating that one in an air valve?
Thanks,
Dave
(By radiator, I mean the kinds with a row of sheet metal fins enclosed in a metal housing, not the big cast iron radiators of old.)
There are 8 radiators in my house and not 8 steam lines leaving the boiler, so I know that radiators can share a steam line.
Can I "T" the steam line? What are the issues/problems?
Do I simply need to use a "Y" instead of a "T" so the water can run back down?
If I can't "T" the radiators, can I feed one radiator, then pipe out of that radiator a short distance through the wall into the second radiator, terminating that one in an air valve?
Thanks,
Dave
0
Comments
-
Sounds to me
that you aren't adding any radiation at all but merely splitting it into two half sized loads. Then you can T it. You should think about using a vent on each line that is of a "slower" rate (smaller orifice) since you will now have two vents on that riser instead of 1. This can change the system balance in a way you may not like. Or use the same kind of vent and see how it works. I'd say its a good idea to have the two vents identical, though.
-TerryTerry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements