\"Splitting\" a Steam Radiator

Dave_127
Member Posts: 18
I have one-pipe steam heat in my 50-year-old house. I am splitting the upstairs bedroom farthest from the boiler into two rooms. I would like to "T" the steam line that goes to the current single radiator to supply two radiators, one in each room. My plumber says you can't "T" a steam line.
(By radiator, I mean the kinds with a row of sheet metal fins enclosed in a metal housing, not the big cast iron radiators of old.)
There are 8 radiators in my house and not 8 steam lines leaving the boiler, so I know that radiators can share a steam line.
Can I "T" the steam line? What are the issues/problems?
Do I simply need to use a "Y" instead of a "T" so the water can run back down?
If I can't "T" the radiators, can I feed one radiator, then pipe out of that radiator a short distance through the wall into the second radiator, terminating that one in an air valve?
Thanks,
Dave
(By radiator, I mean the kinds with a row of sheet metal fins enclosed in a metal housing, not the big cast iron radiators of old.)
There are 8 radiators in my house and not 8 steam lines leaving the boiler, so I know that radiators can share a steam line.
Can I "T" the steam line? What are the issues/problems?
Do I simply need to use a "Y" instead of a "T" so the water can run back down?
If I can't "T" the radiators, can I feed one radiator, then pipe out of that radiator a short distance through the wall into the second radiator, terminating that one in an air valve?
Thanks,
Dave
0
Comments
-
Sounds to me
that you aren't adding any radiation at all but merely splitting it into two half sized loads. Then you can T it. You should think about using a vent on each line that is of a "slower" rate (smaller orifice) since you will now have two vents on that riser instead of 1. This can change the system balance in a way you may not like. Or use the same kind of vent and see how it works. I'd say its a good idea to have the two vents identical, though.
-TerryTerry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements