Slant Fin Sentinal
Pilot stays lit circs all work, have 24v from transformer but draft hood not opening. when rotated just a little it starts rotating a full circle from closed to open to back closed. No green light ever comes on on the hood control panel/motor. need to get this pup to fire.0 -
Sounds like,
something isn`t wired correctly. What make of VD is it? Effikal, Johnson?
Dave0 -
it was wired different!
Ok i called someone who is good at wiring and it turns out the low v low water guard dog was faulty. It showed a green lite (fooled me) It was wired as to make tracing a little more difficult, but not for him! and thank you Dave, Dave0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements