Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Slant Fin Sentinal

Bob Flanagan_3
Member Posts: 67
Dave:
Any other questions, give us a call at 1-800-873-4346.
Hope all else is well.
Bob Flanagan
Director of Sales
Slant/Fin Corp.
Any other questions, give us a call at 1-800-873-4346.
Hope all else is well.
Bob Flanagan
Director of Sales
Slant/Fin Corp.
There was an error rendering this rich post.
0
Comments
-
Slant Fin Sentinal
Pilot stays lit circs all work, have 24v from transformer but draft hood not opening. when rotated just a little it starts rotating a full circle from closed to open to back closed. No green light ever comes on on the hood control panel/motor. need to get this pup to fire.0 -
Sounds like,
something isn`t wired correctly. What make of VD is it? Effikal, Johnson?
Dave0 -
it was wired different!
Ok i called someone who is good at wiring and it turns out the low v low water guard dog was faulty. It showed a green lite (fooled me) It was wired as to make tracing a little more difficult, but not for him! and thank you Dave, Dave0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements