Slant Fin Sentinal

Dave:

Any other questions, give us a call at 1-800-873-4346.

Hope all else is well.

Bob Flanagan
Director of Sales
Slant/Fin Corp.

There was an error rendering this rich post.

Comments

  • Dave_94
    Dave_94 Member Posts: 17
    Slant Fin Sentinal

    Pilot stays lit circs all work, have 24v from transformer but draft hood not opening. when rotated just a little it starts rotating a full circle from closed to open to back closed. No green light ever comes on on the hood control panel/motor. need to get this pup to fire.
  • Sounds like,

    something isn`t wired correctly. What make of VD is it? Effikal, Johnson?

    Dave
  • Dave_94
    Dave_94 Member Posts: 17
    it was wired different!

    Ok i called someone who is good at wiring and it turns out the low v low water guard dog was faulty. It showed a green lite (fooled me) It was wired as to make tracing a little more difficult, but not for him! and thank you Dave, Dave