air valve
Options
joe plumber
Member Posts: 2
would a air valve work in a 2 pipe syst.
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....
0
Comments
-
would it work
would a air valve work in a 2 pipe syst.
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....0 -
No!
Find out why the rads don't get hot. Disconnect the unions at the traps and see if they heat. If so, you have pressure in the returns- possibly from bad traps elsewhere in the system- or a water pocket in the return. If not, something is blocking the steam supply- possibly a water pocket there too.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements