Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
air valve
joe plumber
Member Posts: 2
would a air valve work in a 2 pipe syst.
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....
0
Comments
-
would it work
would a air valve work in a 2 pipe syst.
have 2 rads. twined in and not getting hot.
changed 2 traps and valve... stm going to all other rads
help....0 -
No!
Find out why the rads don't get hot. Disconnect the unions at the traps and see if they heat. If so, you have pressure in the returns- possibly from bad traps elsewhere in the system- or a water pocket in the return. If not, something is blocking the steam supply- possibly a water pocket there too.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements