Best 88% Oiler
88% and not a problem yet.
  • Eric L._2
    Eric L._2 Member Posts: 94
    What brand is that?
  • psd_3
    psd_3 Member Posts: 86
    With an NX burner
    aka ... Beckett
  • Cut your fuel by an easy 30%
    Install a Slant-Fin. Today.
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    stack temp is....
    289F??? You could very well have flue/chimney isses very soon...what type of a liner is it or was it...? kpc
  • The flue pipe and stack are dry as can be.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,687
    rw
    I'd like to know who you are. Please email me at mailroom@heatinghelp.com. Thank you.
    Retired and loving it.
  • dana_3
    dana_3 Member Posts: 57
    boiler
    at 10.9% co2and 41% excess air. that isn't that good. at what percent co2 does it start to run at a trace of smoke.
  • Weezbo
    Weezbo Member Posts: 6,231
    the one that i installed ,
    has a Riello.
    it sounds and acts very much like a Viessmann chassis burner.
    everything just purrs along like a kitty cat :)
    it is radiant with an instantaneous water heater (pinner indirect) out of triangle tube lane by way of Keller
    I think the Slant -Fin ,Eutectic, is an exceptional value.
  • Weezbo Exceptional Value
    Is an understatement.
    As far a smoke, it has no trace of smoke and never did. After a few tanks of fuel the flue connector to the chimney has no visible or detectable soot whatsoever period.
  • Weezbo
    i like the way you practise wisdom.
    that young ladd has a great deal of admiration in his eyes for you. Way to be. i read .between the lines, a lot.
  • deville
    deville Member Posts: 10
    Looks fishy to me
    Excess air at 41%,10.9 CO2 and 88% combustion eff? The only way that would be possible is that either it is a condensing boiler or you took your reading as soon as you fired it with your water temp at 90 degrees. If it is a true reading with your water temp up above 140 then you should be able to get your EA dialed in to 30%, CO2 12% and should be above 90%. I find that very hard to believe in a standard 3-pass design. I'm not knocking the boiler, they look to be a good piece of equipment, I'm just questioning the presentation of the data.
  • Blame Testo
    The water temperature was above 160 ish and below 180 during the test. It has to run there because we are a little short on baseboard. The boiler has about 15 minute run cycle when it is cold. Easy to get a test done in the mid cycle time.
    Yes it is a 3 pass. The smallest they make.
    The data is from Testo. I prefer Bacharach, but that's that.
  • deville
    Why the high excess air?
    I'll certainly look into these little miracles then.
    Why the high excess air? Did you try cutting the air back and getting the CO2 up to around 12%? Seems like if it performs that well were it is it would be nothing short of phenomenal dialed in.
    Does this boiler have any special internal mixing or or stainless combustion cylinder?
  • Nothing fancy except the skin
    A little excess air is nice for times of low draft (spring & fall) start-ups.
    No special mixing or stainless. That's the beauty of the unit.
  • deville
    Tried one
    One of the distributors I buy from was on me to try one forever and I finally put one in a few weeks ago, it was O.K, I didn't get the combustion reading your are claiming. The performance was very similar to a Buderus G115 or a Burnham MPO that I am used to. I have nothing against it, it just didn't show me anything to make me jump ship.
  • deville
    Low Temp
    Can it except low temp returns like a Burnham or Buderus?
  • Andy L
    You should have got those readings it's rated at 87% right out of the crate. Nobody's sheet-metal even gets close especially for the price range. Dollar for dollar nothing gets close period.
  • deville
    AFUE
    It's rated 87% AFUE out of the box, combustion efficiency is a totally different number, it's only one piece of the equation. Like I said, it was a nice little boiler but it's not magic!!
  • deville
    Not so....
    Actually the New Yorker FR-HGS has a rating of 87.8% AFUE out of the box and is less than the EC. Be careful with your marketing claims.
  • Kevin__Flynn
    Kevin__Flynn Member Posts: 74
    where was the wand, rw
    Where was the wand inserted in the smoke pipe? Before or after the barometric?
    Kevin Flynn
  • Right Here
  • I put in a Utica Oil Boiler
    energystar rated, and AFUE rated at 86% and that is exactly the reading I got on my old Fryrite combustion analyizer. Thanks, Bob Gagnon
  • Combustion Numbers @ 190*F
    Not too much difference.