outdoor reset control
Brent_2
Member Posts: 81
Hi
I am looking for an inexpensive outdoor reset control. This is for a single radiant zone addition in a existing hot water baseboard home. I was planning on using a 3 way mixing valve.
thanks
Brent
thanks
Brent
Taco iValve
Brent --
You might like this one. The iValve is a motorized 3(or 2, or 4) way mixing valve with a full outdoor reset control built in. Take a look, and feel free to e-mail me if you have any questions. Good luck...
JMB
http://www.taco-hvac.com/en/products/iSeries Mixing Valves/products.html?current_category=1880 -
Beat me to it, JB
Taco i-Valve.
Done.0 -
3 ways
I use the Taco ISeries.0 -
That
would likely be a great place for a 4 way I series R from Taco *~/:)0 -
Weezbo raises an excellent point
The 4-way will afford at least some boiler return water protection whereas the 3-way may allow extended periods of cooler return water. The system description does say "existing baseboard system", so the presumption of a non-condensing boiler exists as a strong possibility.
A condensing boiler favors a 3-way valve to avoid sending excess hot water supply back to the boiler. The 4-way will.
Good call, Weez!0 -
zone valve
do any of these Tacos look at indoor temp?
Not directly, no.
The i-Valve Reset series looks at ODT and HWS temperatures to set the curve. Optionally, boiler return is used as a low-limit protection function which over-rides the HWS setpoint, I believe.
Indoor temperature is governed by the space thermostat, ideally via a Taco Expandable Relay.0
- 120 Geothermal