F09 Munchkin VWH
Guy = Crap
  • vhlaundry
    vhlaundry Member Posts: 41
    F09 Munchkin VWH
    I just installed 2 munchkin VWH 199Btu with a 200gal storage and they ran fine for a day. Now one unit works and the other has a F09 code. This is what i done so far:
    Checked Ignitor and i have spark
    Check condensate line for blockage
    Removed exhaust and some water came out.
    Any suggestions?
  • Canasta Pete_2
    Canasta Pete_2 Member Posts: 18
    This is what you have to do
    NEVER EVER install a Munchkin again. The F09 is on the wall every other day. Install Buderus GB142's and you will never have a callback. The Munchkin is a failed experiment that has cost Tech's thousands of lost man hours due to failures. They should send a Labor Allowance in the box!
    My 2 cents
    O'l Canasta
    (31 years in the trade and still counting)
  • Guy_6
    Guy_6 Member Posts: 450
    F09
    Oddly enough, every F09 that I encountered during my stint at HTP was due to either an improperly installed or improperly set up boiler. Although every boiler is run at the factory, field conditions differ. Combustion testing and fine tuning upon startup is a simple way to assure that the good quality boiler that you have installed delivers what it promised. And that goes for any boiler.
  • Canasta Pete_2
    You are only fooling yourself
    F09 is a legend and you and everyone else knows it. I am surprised that since you no longer sell them that you would stick up for a product that has been left in the dust by superior manufacturers. Wave as the bus goes by because you missed it.
    O'l Canasta
  • Guy_6
    Ok
    That's fine if that's what you want to believe. I still believe in the quality of that product and not every product will satisfy every person. Did you do combustion testing on your "problem " boiler?
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    And/or....
    Check for what I've been told is the most prevelent problem...the lack of a vent hole in the top of the trap?
    Fixed more than one of my F-09 lockouts. Until you've walked a few miles in someone elses moccasins, don't be causing blisters without powdering first. Chris
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Uh........Guy
    "Every" is a pretty strong statement.
    You wanna' stick with that?
    Mark H
  • mr bull
    mr bull Member Posts: 15
    I could not agree more with your comments about Munchkin. I too have worked many days on Munckins at the home owners expence. Systems that have been installed by the cheeper bid. Not so cheep after all. Good luck
  • Mark Hunt
    Now honestly
    who helped you with the big words?
    WATCH OUT!!!!!!!!!!! PING PONG BALLS!!!!!!
    HAHAHAHHAHAHA!!!
    Gotcha' again Mr.BS!
    Mark H
  • Mr. Ed
    Mr. Ed Member Posts: 2
    Munchie
    Munchie = CRAP
  • vhlaundry
    Thanks for everyones help we got the boiler working today. The condensate backed up into the boiler and was causing the ignitor to arc onto the wet insulation. The unit is installed on the ground and the condensate was not draining properly. We removed the bracket that holds the trap onto the back of the unit and now we have a nice flow. I hope this unit remains trouble free and saves me some natural gas. I also would like to add that Chuck at Htproducts was very helpful.
    Thanks
  • Rookie
    Rookie Member Posts: 175
    How much time
    Guy since you believe all the Munchkin problems are contractor related, how much extra time, should I add in to the installation cost, for call backs.Not trying to be a wise ****, but I have been down that road, a lot of time invested, not because of contractor error, I resent that remark.Better yet, how many hours did you trouble shoot the Munchkin or the Voyager boiler, without getting paid for it?
  • zurnie
    zurnie Member Posts: 8
    Having been involved with several 100 Munchkin installations over the past few years. I can assure you, all Fo9 codes are due to lack of following the installation instructions for venting,draining and Co,Co2
    settings. Don't blame the builder if the contractor can't
    install it right. Follow the instructions, its simple and it works