Ratings on Valves
... can be either working steam pressure, or wet (as in not superheated) steam pressure, depending upon who's definition you're looking at. Either way, it's for saturated steam, not superheated.
  • Supply House Rick
    Supply House Rick Member Posts: 1,399
    WSP Rating on Ball Valves
    WSP: Working Steam Pressure
    Can a ball valve with this rating be used in a commercial kitchen on LP gas fed appliances?
    A customer of ours states the Gas Company left these for him to make the connections. Any thoughts? Thank you for your help...
    Rick
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Valves
    The proper rating is "WOG" -water, oil or gas.
    Use valves specifically made for natural gas.
    WSP I always believed is "water service pressure" but I may be wrong. But they are clearly not a gas-rated valve.
  • Tony Conner_2
    Tony Conner_2 Member Posts: 443
    \"WSP\"...
    Not all ball valves will be rated for natural gas service.
  • Brad White_9
    Thanks, Tony
    Always learning...
  • Supply House Rick
    Is That
    A yes or no?
  • Tony Conner_2
    I Would...
    ... say that unless it's got some other marking, and/or a piece of paper indicating that it's been approved for gas installations, it would be "no".
  • Supply House Rick
    Can Anybody
    Give me a straight accurate answer and back it up with documentation? This could save lives...
    Thanks,
    Rick
  • John Starcher_4
    John Starcher_4 Member Posts: 794
    Rick,
    If you know the valve manufacturer, why not contact them directly? This way you will get a definitive answer.
    Starch
  • bob young
    bob young Member Posts: 2,177
    a.g.a.
    on a recent installation of a weil-mclain commercial boiler a brass ball valve was factory furnished with the gas train. this seemed odd to me but weil-mclain knows best. i have always used a.g.a. rated valves for gas. on larger sizes [2 " & up ] plug valves are usually speced out. not sure if they are a.g.a. rated but are sure serious and costly.
  • Supply House Rick
    Not sure of MFG
    A customer of ours posed this question to me. I called around, no one will put it in writing. Why? I have heard responses from mfg's ranging from no to maybe to yes...
  • hr
    hr Member Posts: 6,106
    The valve manufacture
    will be able to supply a copy of all the listings for their valves.
    Virtually every valve has a name tag or their name molded in the body somewhere.
    I agree if it is used for gas service it should have those listings.
    I use a lot of Jomar brand an have the cut sheets that show AGA, FM, UL and various others depending on the model of valve I chose.
    If it's a nameless import you may be in for a "hunt"
    hot rod
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,712
    Brad,
    check out the Acronyms of the Industry in Hot Tech Topics. Dozens of us put that together a few years ago.
    It pays to wander off the Wall.
    Retired and loving it.
  • Tony Conner
    Tony Conner Member Posts: 549
    What Does...
    ... the fuel utilization code for your jurisdiction say? The onus is on the owner/designer/installer to ensure that bits they're assembling meet the various codes & regulations. Any or all of these people have an obligation to ensure that the components they're using meet whatever code applies. This means asking the manufacturers to provide documentation showing proof of approvals by the inspection authority. No documentation means no approval means "no cigar". A manufacturer can't say "Show me where it says that I don't have the required approval". It doesn't work that way. The burden of proof lies with the manufacturer.
  • mark  smith
    mark smith Member Posts: 112
    you CAN use a WOG rated valve, if supplied by the Mfgr.
    otherwise, AGA rated is the only approval for nat gas
  • bob young
    manufacturer vs. code
    weil-mclain also supplies assorted bushings for their gas trains. any thoughts on that ?