snow melt
Yes, the tubing was installed several years ago and left with a pressure test on it.
The centers are apox., 6-8 inches.
  • Robert O'Connor_12
    Robert O'Connor_12 Member Posts: 728
    temperature
    What would be the maximum temperature allowable in a snow melt glycol job.
    I can mix the temp down before the HX to anything I'd like BTW.
    also, what would be a reasonable difference between supply and return temperatures on the glycol side?
    There is only one loop of 1/2 inch apox 200 feet long and roughly between 30 & 40 % glycol.
    Thank You!
  • EtienneHancock
    EtienneHancock Member Posts: 18
    Is the
    tubing already installed? Do you know what the on center distances for the loops if so?
    temp
    anyone??
  • Couderay
    Couderay Member Posts: 314
    Snow melt temp.
    I would say 130*F if in concrete