snow melt
Robert O'Connor_12
Member Posts: 728
Yes, the tubing was installed several years ago and left with a pressure test on it.
The centers are apox., 6-8 inches.
temperature
What would be the maximum temperature allowable in a snow melt glycol job.
I can mix the temp down before the HX to anything I'd like BTW.
also, what would be a reasonable difference between supply and return temperatures on the glycol side?
There is only one loop of 1/2 inch apox 200 feet long and roughly between 30 & 40 % glycol.
Thank You!
Is the
tubing already installed? Do you know what the on center distances for the loops if so?0 -
temp
anyone??0 -
Snow melt temp.
I would say 130*F if in concrete0