  • 3/4 Pex

    What is the maximum BTU's that 3/4 pex can put out. The boiler is about 15' from the Air handler. I left my book at the office.....Thanks Anthony
  • Joe Brix
    Joe Brix Member Posts: 626
    3/4 piping

    can deliver 40K BTU @ 4GPM I believe.
  • Jim_65
    Jim_65 Member Posts: 184
    3/4\" Pex

    Approximately 3/4" can carry 40,000 Btu's (4 gpm) at a 20 degree delta T.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Sounds like

    a consensus! 4 gpm, 40 MBH....
  • Jerry_15
    Jerry_15 Member Posts: 379


    You can alway push it with a bigger pump, especially on a short run like that, and get more BTU's, but why bother? Check the requirements on the coil, if it has 1" connections, and you actually have a demand and flow requirements, why fool around?
  • Jim_65
    Jim_65 Member Posts: 184


    I didn't mean to reiterate what was already posted. I just wanted to state it is the gpm was dependant on Delta T.
  • Brad White_9
    Brad White_9 Member Posts: 2,440


    I know, just having fun. You are of course, correct. Nice universal poll with all the parts explained.

    Thanks Jim

    Brad