Poly Butalene hydronic system and CI boiler;
George_10
George_10 Member Posts: 580
Clean the system with our Hydro-Solv 9100 and then treat it with our Pro-Tek 922. The treatment product contains an oxygen scavenger as one of its ingredients.
You can contact us at 800-543-5975.
Ask for George or Dwight.
Hope this helps.
George
  • G Lyons
    G Lyons Member Posts: 36
    Poly Butalene pipe and CI boiler
    There was an inhibitor solution for these systems a few years ago. Is there still aproduct to counteract the oxygen. Or what needs to be done? This is a 12 year old system and is still OK but what is happeing inside? The pink solution that was being used seams not to be available now. George, and thanks for your input...
  • G Lyons
  • Weezbo
    Weezbo Member Posts: 6,231
    Flat PlateHeat Exchanger avec 90 ->100 degree water ...
    with strainer on the plate would be a Good idea as would flushing the system and boiler. then get a hold on our Romar Guy *~/:) hes the dude:)
  • hr
    hr Member Posts: 6,106
    With a PB
    system you will need to check and boost the O2 inhibitor. the higher the temperature the system operates the more O2 ingress.
    Ususlly the thin metal components fail first. High temperature PB systems will eat expansion tanks first.
    hot rod
  • G Lyons
    P.B. C.I. boiler, baseboard radiation help. Thanks!
    Thank you gentlemen for your input.