tripping circuit breaker
 
            
                
                    Brad White_9                
                
                    Member Posts: 2,440                
            
                        
            
                    Goodman Customer... 
"A Goodman customer walks into a bar...." I can think of the possibilities. But every system has it's price point.
:)
BTW: Ed can buy one and get's to keep it when he is done. If not borrow one.... Ed- See Marty at Interstate in Brighton.
                "A Goodman customer walks into a bar...." I can think of the possibilities. But every system has it's price point.
:)
BTW: Ed can buy one and get's to keep it when he is done. If not borrow one.... Ed- See Marty at Interstate in Brighton.
0                
            Comments
- 
            tripping circuit breaker
 10 yr old goodman 24,000 btu a/c conderser on occasion circuit breaker trips any ideas on finding the problem trips at differant times cant be there 24/7 to watch the problem
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            
 Ed,
 Try installing a time delay relay in condenser wiring compartment on 24v signal . If they have a non-digital tstat it could be tripping because of people fooling w/ the it, not giving it time to equalize pressure before next start-up.
 Whats the amp draw?? I bet you'll be needing a capacitor soon.30/5 370 volt I believe.
 Good luck, Tom0
- 
            A few things come to mind
 Locked rotor on compressor, short circuit (squirrel chewing a wire does wonders for your remaining hair), water in system such as a conduit pigtail, breaker may have arced a few times and need to be replaced.
 I would get a data logger with amperage reading, see what trip point is. May be a voltage drop in the system or elsewhere which increases the amperage above limit.
 I imagine this is a 220V setup?0
- 
            A what?
 A data logger did you say? Good luck with trying to charge a goodman customer for that.
 I'm sorry just clowning alittle bit..please forgive me.
 I'm with you guys..capacitor,loose wires and, maybe a burnt breaker at the panel box.Plese remove breaker and check for burnt marks on the back of it.
 And one more thing if she has a fan delay relay on her please replace that as well because, it just a matter of time and you will get a call for a frozen up unit.0
- 
            Yours
 was better..LOL.0
- 
            Circuit Breakers
 Evening Ed!Low volt connection inside wire nut broken causing chattering or ,is the C.B.panel located in a hot area,like a garage? Or one of the other ideas allready stated! Let us all know what you find out after you fix the problem.Enjoy!0
- 
            Could be ANYTHING...
 We need some measurements and a basic explanation where you think it is coming from. What is the FLA when everything is running? Pressures and temps would also help. Breakers DO FAIL, but I will not jump to conclusions here. Have you checked you run CAP?////mfd rating? How do the contacts on the contactor look? What kind of stat, with TDL or not? Why even tackle this if there is no INFO...? It's like saying I have no A/C,..What is the problem.....
 Mike T.0
- 
            type
 One more thing, is the breaker a HCAR type? The nameplate on the cond. unit usually requires a HCAR rated breaker.0
- 
            No A/C
 If all other things look good, I'd check the line voltage connections at the unit and in the panel. Also, if the customer is on the end of a street where there has been a lot of developement(no permits pulled on electrical equipment)you could be suffering a voltage drop at peak usage times. Breakers are cheaper than data loggers:)0
- 
            Yeah, but
 the damage caused by oversizing a breaker for a suspected voltage drop condition might have if it exceed the protective threshold of the equipment... (in case you were anticipating up-sizing the breaker and not that you were)....
 Data Loggers Rule 
 Your point about development and voltage drop is excellent by the way.
 Brad0
- 
            Thanks Mike...
 The list of possible causes for a tripped circuit breaker is ENDLESS.
 Hope you find the end very soon.
 Best of luck.0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements