R-22 VS 410-A
In my opinion, KEEP the 7/8 & 3/8" line. What is the problem with R22? You can go aprox....100' with some provisions to assure oil back to the compressor. 3 ton, if that is what you want,...Do it. Contrary to belief, The further you go..At least with the LL you will need to down size to keep your velocity, but your application is not unusual. Long, but not unusual..
Mike T.
  • Gasper
    Gasper Member Posts: 148
    R-22 VS 410-A
    We have to fix someone elses bad work. It's a Unico system with a 75'(plus) lineset(7/8" X 3/8"), with a 25' rise. My supplier says 410-A can handle a longer lineset compared to r-22. What do you think? (To run a new lineset would add a huge cost to this job.) We were thinking of leaving the lineset, adding oil traps, and changing out the condenser, and Unico equipment to 3 ton. Thank You
  • tom_49
    tom_49 Member Posts: 267
    long lines
    Pat,
    w/ 410a we have run lines 175' long in accordance w/ manufactures specs ( Carrier ). No problems.
  • Gasper
    Planning on a Arcoaire
    I just don't know why the last compressor failed. Can a condenser ever be slighty larger then the a-coil?
  • Techman
    Techman Member Posts: 2,143
    Patrick
    Morning! Slightly undersized Evap to cond ratio?You are working on a system that has that setup now! Unico 's Engineering Guide shows for a 1 ton(12k) cond you get 10k BTU's out of the "system" , a 3 ton (36k)cond and you get 27k out of the "system" , and for a 5 ton cond you get 51k out of the "system". the lower rating is based on the normally lower evap temp pulling out more moisture than a convential ,and, better sealed duct work with more air reaching the conditioned space .410a and the POE oil mix so well together that longer line sets are now normal without the need of oil traps in the suction line.Enjoy your day!
  • subcooler
    subcooler Member Posts: 140
    175' line set
    To bad your 13 seer just ended up below 10 seer.
    We even try to avoid that even on refrigeration lines.