Vitodens 100
Tom Hopkins
Tom Hopkins Member Posts: 554
I have been reading through the Votodens 100 literature as I am about to install my first one. I have installed many of the 200 models with the sophisticated on board controls and and am trying to figure out the following:
Does the 100 output 1 single temp for DHW AND heating, requiring that it be mixed down for radiant floors, or are there 2) setpoints; 1 for Heating and 1 for DHW.
If the boiler is outputting 160°+ all the time it would not seem to be able to condense like a Vitodens 200 outputting 95°.
Are there 2 different tt connections like a Trinity, one for DHW and one for heating?
I cannot seem to find the answer in the literature.
Who has installed one of these in a combined installaion? Impressions?
Thanks.
  • Josh_10
    Josh_10 Member Posts: 786
    Nope.. One single temperature. It has an extra input for DHW but it doesn't have two temps. I understand that there is a remote 0-10V module you can install now to remotely modulate the boiler though.
    Also as I am sure you are aware from the 200's-- the venting is tough.
  • S.H
    S.H Member Posts: 1
    Vitodens help
    So Cal,
    Call me @ 1-877-853-3288 on Monday morning. This is the toll free number to Viessmann BC. I will explain how it works. Please ask for Stuart. Call after 8:30 am.
  • Leo G_101
    Leo G_101 Member Posts: 87
    Yes
    there are 2 TT connections. One is for floor heating, with a reostat dial on the front panel, can set to temp. The other is for DHW/high temp. When closed, the boiler ignores the low temp tt, and fires up to about 176*.
    The wiring diagram should be attached to the inside of the cover. Very easy to read and wire.
    Instead of using a time delay relay, to purge the boiler after hi temp use, i used a Taco RMB.
    Leo G