Vitodens 100
Tom Hopkins
Member Posts: 554
I have been reading through the Votodens 100 literature as I am about to install my first one. I have installed many of the 200 models with the sophisticated on board controls and and am trying to figure out the following:
Does the 100 output 1 single temp for DHW AND heating, requiring that it be mixed down for radiant floors, or are there 2) setpoints; 1 for Heating and 1 for DHW.
If the boiler is outputting 160°+ all the time it would not seem to be able to condense like a Vitodens 200 outputting 95°.
Are there 2 different tt connections like a Trinity, one for DHW and one for heating?
I cannot seem to find the answer in the literature.
Who has installed one of these in a combined installaion? Impressions?
Thanks.
Does the 100 output 1 single temp for DHW AND heating, requiring that it be mixed down for radiant floors, or are there 2) setpoints; 1 for Heating and 1 for DHW.
If the boiler is outputting 160°+ all the time it would not seem to be able to condense like a Vitodens 200 outputting 95°.
Are there 2 different tt connections like a Trinity, one for DHW and one for heating?
I cannot seem to find the answer in the literature.
Who has installed one of these in a combined installaion? Impressions?
Thanks.
0
Comments
-
Nope.. One single temperature. It has an extra input for DHW but it doesn't have two temps. I understand that there is a remote 0-10V module you can install now to remotely modulate the boiler though.
Also as I am sure you are aware from the 200's-- the venting is tough.0 -
Vitodens help
So Cal,
Call me @ 1-877-853-3288 on Monday morning. This is the toll free number to Viessmann BC. I will explain how it works. Please ask for Stuart. Call after 8:30 am.0 -
Yes
there are 2 TT connections. One is for floor heating, with a reostat dial on the front panel, can set to temp. The other is for DHW/high temp. When closed, the boiler ignores the low temp tt, and fires up to about 176*.
The wiring diagram should be attached to the inside of the cover. Very easy to read and wire.
Instead of using a time delay relay, to purge the boiler after hi temp use, i used a Taco RMB.
Leo G0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements