oil burner problem
doug_28
doug_28 Member Posts: 1
i have been trying to find why a ecoflam minor 8 oil burner is malfunctioning. the difficulty is the burner runs perfectly 95% of the time. i was at this client's residence five time for a total of four hours before the buner actually malfunctioned. the problem is the burner does not ignite smoothly and it will then sputter and shut off. i wait and press the reset button and it will ignite and run smoothly for hours. i checked the fuel pressure on the fuel pump and the pressure does not fluctuate when the burner is running. i cleaned all filters and changed the nozzle. i changed the coupling for the fuel pump and changed the flexible hoses connecting to the fuel pump. any suggestions? thankyou
  • Bill Nye_2
    Bill Nye_2 Member Posts: 538
    Did You......
    Did you put a vacuum gauge on the supply pipe to the burner? What did you have for a vacuum reading?
    Steamhead Member Posts: 17,899
    If the vacuum checks OK as Bill suggested
    I'd install a delayed oil valve. This keeps oil from reaching the nozzle until the pump and fan are up to speed and air is moving thru the firing zone. These units give good, clean, consistent starts especially on newer boilers with smaller firing zones.
    Consulting
  • soot_seeker_2
    soot_seeker_2 Member Posts: 228
    what about?
    what about?
    intermittently bad ignitor or failing transformer.
    hair line cracked Porcelain electrode shorting to ground.
  • Firedragon_4
    Firedragon_4 Member Posts: 1,434
    Hi Doug,
    just one question. Where are you located? The EcoFlam is not available in the US. Haven't heard that name since my last trip to Italy.
  • Al Gregory
    Al Gregory Member Posts: 259
    I say oil pump
  • Weezbo
    Weezbo Member Posts: 6,231
    al i think you are probably right....
    sad to say these new style pumps are a veritable POS...normally id say that a delayed oil valve would help,as would a quick check of the nozzel holder. simply lash up a pressure gauge to the nozzel holder....i have seen hairline cracks cause that ...it is very difficult to see it some times as the nozzel holder so seldom is cracked and also because the malfunction isnt something that jumps right out at you...