Veha panel radiators. purging air
Options
Chip_8
Member Posts: 22
I have a customer with a third floor apartment that has constant trouble with air in his panel radiators. The boiler is in the basement, has the pump on the return side, and has an expantion tank upside down in a tee right above the pump. Another guy from our shop purged the snot out of it from the basement and bled the coins on the tops of the rads, and it still gurgles. The only thing I could think was the bladder was bad on the tank, but I checked it and all seems well. The rads are piped supply into the top and return into the bottom, backwards right????? Thanks, Chip
0
Comments
-
Hot water radiators
No a hot water radiator can be supplied at the top and return from the bottom or supplied and returned from the bottom but never a return on top.
If you only have one zone .........repipe in a air scoop before the cirulator and after the extrol connection. More then one repipe circulators and air scoop on supply .
Also hang the tank down sticking up on a heating pipe acts like a air bank .. Deposits and with draws air with a change in pressure.There was an error rendering this rich post.
0 -
how much....
air pressure is in the extrol?0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements