Veha panel radiators. purging air
Chip_8
Chip_8 Member Posts: 15
I have a customer with a third floor apartment that has constant trouble with air in his panel radiators. The boiler is in the basement, has the pump on the return side, and has an expantion tank upside down in a tee right above the pump. Another guy from our shop purged the snot out of it from the basement and bled the coins on the tops of the rads, and it still gurgles. The only thing I could think was the bladder was bad on the tank, but I checked it and all seems well. The rads are piped supply into the top and return into the bottom, backwards right????? Thanks, Chip
  • Big Ed_4
    Big Ed_4 Member Posts: 3,205
    Hot water radiators
    No a hot water radiator can be supplied at the top and return from the bottom or supplied and returned from the bottom but never a return on top.
    If you only have one zone .........repipe in a air scoop before the cirulator and after the extrol connection. More then one repipe circulators and air scoop on supply .
    Also hang the tank down sticking up on a heating pipe acts like a air bank .. Deposits and with draws air with a change in pressure.
  • kpc_34
    kpc_34 Member Posts: 12
    how much....
    air pressure is in the extrol?