the returns might join together above the boiler's waterline. If so, that's what's messing up the south loop and the tail- it's getting air from two directions.
If this is the case, drop all the returns below the waterline before teeing them together. Then, properly vent each main and the tail too- I think you could have the tail vent take care of the whole south main- and it should work fine.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
I'm looking for a distributor in Michigan that handles Gorton steam vents. Specifically, I need #2'a and 6's. Anyone out there??0 -
Steve, you can get them
from State Supply online, www.statesupply.com . Not sure if a supply house up your way has them, but Ken Kunz at Gorton could tell you- 908-276-1323.
Steve, checkout this link: http://www.pexsupply.com/Categories.asp?cID=302&brandid=
I've bought from there several times with good results. I'm in Bay City, Michigan0 -
Thanks guys
I looked a steam system that has some messed up piping last week but I think better venting will help it out some.
I'll do my best to describe it and post some pics which will hopefully give some clues as to what I'm talking about.
Coming off the riser, the piping splits and forms two loops which serve the north and south half of this two story home. The issue the homeowner is having relates to three rooms on the south loop. The north loop heats adequately but the last three rads on the South loop take forever to heat even with the vents removed from the rads.
The north loop is laid out as you would expect to see, making an uninterrupted circuit from the boiler back to the Hartford loop. The South loop however has a "tail" which t's off as the loop makes its way back to the boiler. (All the rads are single pipe BTW.) The "tail" does have a Dole vent in the main, which is reduced to 1 1/2" by that point. Two of the rads that don't heat are on the second floor and all three are on the "tail" section. I did find what I think will prove to be a main vent location that was plugged off on the riser going to one of the second floor rads.
I'm thinking that a couple Gortons would help get the air out of this "tail" and help those three orphaned rads to heat at least a little better. The only other option I can see, at least if I'm barking up the right tree here, would be to install an equalizer loop of some kind from the tail all the way back to the Hartford loop.
Pics 739 and 740 show the near boiler piping
Pic 741 shows the risers for the last two rads that heat OK on the South loop. The line going back across the picture to the left hits the return going back to the boiler.
742 shows the line from 741 T'd into the return. The three rads that don't heat are on the line you can see going through the back wall.
743 shows the vent currently on the poorly functioning section on the other side of the wall shown in 742.
744 is sideways but shows the "tail" looking back toward the tee in 742.
745...ignore
746 is also looking at the tail from the view you would have standing by the last radiator riser looking back toward the boiler and the Tee shown in 7420 -
Hmmm
I can't say that I noticed that when I was there but I may go back and check it out again. I can see where you would say that looking at the picture (740?)0 -
That one and 742
though one would really have to be there to make sure.
Picture 742 is the bottleneck.....I think
The steam is coming into the bull of the tee as shown in the picture. The back of the run is the "tail" with the 3 non heating rads on it and the other side of the run is the return headed back to the boiler. It would be the center pipe shown in picture 740.0 -
Where is the vent on that main
in relation to pic 742? I know there's a vent on the tail.....
Do any other return lines connect to the return from the tee in 742 before it drops below the waterline?
Are there any more rads connected to the return from the tee in 742 before it gets back to the boiler?
Might be on to something there
The only vents on the south loop are on the tail0 -
Just an added thought
Steve, check how much radiation is on the loop with the tail. I suspect that the one-pipe tail might have been added after the mains were already sized for the two-pipe system. The size of that steam main might be marginal.
Just a hunch, it would be nice to rule it out.
Noel0 -
It appears
The "tail" is likely an addition to the original piping. The owner mentioned that the back part of the house was attached to the main building at an unknown date many moons ago. The two rads that I saw were smallish in size, maybe 6 column IIRC. One is in the kitchen and the other is on the second floor directly above.0