Stack temperature
Make sure your meter reading is a true " T Nett" reading", flue temp minus ambient. Also when you turn your meter on, it normaly has a countdown auto calibrate time. This normally takes a half minute.
When your meter is counting down, keep the probe end away from parts of the boiler that are above ambient temp. It could be a reason these reading are high. Some meters do give a T nett and T flue reading.
I use a UEI C75 and Testo 325 and are with in 5 deg. of each other any time I put one against another to verify.
  • realolman
    realolman Member Posts: 513
    I just stuck a digital thermometer in the stack of my V74 boiler about 9" above the boiler while it ran for about 5 minutes.
    It went up to 648 deg F.
    Any thoughts or comments?
    thanks
  • clammy
    clammy Member Posts: 3,242
    cleaning time
    With a stack temp at that i would if the boiler is oil fired call for a cleaning and have the chimmey base check .Sounds like it's dirty with a stack at over 600 ,i would have the boiler clean and serviced and a eff test performed peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • realolman
    oil fired
    It is oil fired
  • clammy
    call for service
    Call for service and get it clean make sure they check the combustion chamber and give the burner a good going over also check draft and the draft damper to ensure that it is set up correctly peace and good luck clammy
    NJ Master HVAC Lic.
    Mahwah, NJ
  • Timco
    Timco Member Posts: 3,040
    Good call....lack of draft.
    Just a guy running some pipes.
  • realolman
    just a temp probe
    This is not a combustion analyzer or any thing like that.
    it is just an industrial thermometer with a stainless steel probe.