Flow rate in copper pipes

But if the velocity is too low don't you end up with air trapped at the high sections?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • WV EGBERT_2
    WV EGBERT_2 Member Posts: 98
    Flow rate in baseboard loops

    We are updating an existing heating system that has finned baseboard on the second floor. They are all piped in with ¾ copper.

    In calculating flow rate with a 10° temp drop and the various heat loads I get values ranging from 1.5 to 2 gpm which according to what I can tell is too low to sweep any air bubbles from the system.

    One chart recommends 3.2-6.5 gpm.

    Question: Should we increase the flow rate to say 3.5gpm and let the temp drop fall where it may?

  • kpc_36
    kpc_36 Member Posts: 21
    you're fine.

    you don't want much more than 4 gpm or you will get noise from velocity.
  • kpc_36
    kpc_36 Member Posts: 21
    not if you pipe....

    it properly. Pipe it w/ the circ. pumping away from the expantion tank and leave the pressure @ 18psi. Have you read any of dan's books? kpc
  • WV EGBERT_2
    WV EGBERT_2 Member Posts: 98


    We intend to pipe it as you suggested. It's not that way now.

    The only book I have is "Modern Hydronic Heating" by Siegenthaler which led me to belive I needed a velocity of 2-4 ft/sec.

    More books are good. Can you point me toward "dan's books"?
  • WV EGBERT_2
    WV EGBERT_2 Member Posts: 98
    Outdoor wood boiler

    To complicate things a bit we want to use an outdoor wood boiler from Central Boiler.

    The sales person/installer says we don't need a flat plate heat exchanger even though the wood boiler is vented to the atmosphere. It seems to me that maintaining 18 psi would be a problem with a boiler vented to the atmosphere.

    Any comments on this would be appreciated.
  • kpc_36
    kpc_36 Member Posts: 21
    you need a HX.

    My opinion of these wood boilers is not very high. I am working w/ a friend on one who did not take my advice. It can get very pricey w/ flat plate hx. big circs. and lots o' eco-flex pipe. Pumping away is a great book....
  • k
    k Member Posts: 38
    wood boiler

    have you considered a wood gasification boiler. for in the house. Look at tarm or econoburn