Flow rate in copper pipes
WV EGBERT_2
Member Posts: 98
But if the velocity is too low don't you end up with air trapped at the high sections?
0
Comments
-
Flow rate in baseboard loops
We are updating an existing heating system that has finned baseboard on the second floor. They are all piped in with ¾ copper.
In calculating flow rate with a 10° temp drop and the various heat loads I get values ranging from 1.5 to 2 gpm which according to what I can tell is too low to sweep any air bubbles from the system.
One chart recommends 3.2-6.5 gpm.
Question: Should we increase the flow rate to say 3.5gpm and let the temp drop fall where it may?
0 -
you're fine.
you don't want much more than 4 gpm or you will get noise from velocity.0 -
not if you pipe....
it properly. Pipe it w/ the circ. pumping away from the expantion tank and leave the pressure @ 18psi. Have you read any of dan's books? kpc0 -
We intend to pipe it as you suggested. It's not that way now.
The only book I have is "Modern Hydronic Heating" by Siegenthaler which led me to belive I needed a velocity of 2-4 ft/sec.
More books are good. Can you point me toward "dan's books"?0 -
Outdoor wood boiler
To complicate things a bit we want to use an outdoor wood boiler from Central Boiler.
The sales person/installer says we don't need a flat plate heat exchanger even though the wood boiler is vented to the atmosphere. It seems to me that maintaining 18 psi would be a problem with a boiler vented to the atmosphere.
Any comments on this would be appreciated.0 -
you need a HX.
My opinion of these wood boilers is not very high. I am working w/ a friend on one who did not take my advice. It can get very pricey w/ flat plate hx. big circs. and lots o' eco-flex pipe. Pumping away is a great book....0 -
wood boiler
have you considered a wood gasification boiler. for in the house. Look at tarm or econoburn0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements